Persistent flicker on SRx v4.01 Ports 2/3 with KULP 32 FPP 8.4.1 – test results
Started by ricardo, November 22, 2025, 03:10:25 AM
ricardo
Hi all,
I'm chasing a stubborn flicker issue and would appreciate a sanity check. Here's the setup and everything I've tested, step by step.
Hardware/Software
  • Transmitter: FPP on Kulp32-AB
  • Receiver: Falcon SRx PSU v4.01
    • Smart Receiver mode v2
    • Receiver A (DIP switches 1–4 ON)
    • Single receiver in chain
  • Controller software: FPP v8.4.1 (v8.4 branch)
  • Pixels: WS281x
  • Config pushed from xLights
Symptoms
  • SRx Port 1 and Port 4: rock solid
  • SRx Port 2 (and previously Port 3): heavy flickering
  • Any pixel string that works on Port 1/4 will flicker when moved to Port 2/3
  • Cable lengths and strings are unchanged between tests
Tests performed
  • Eliminate pixel/cable variables
  • Swapped pixel strings between ports without changing cables or lengths.
  • Result: issue follows the SRx physical port (2/3), not the pixels or cabling.
  • Per‑port configuration parity
  • Verified per‑port settings identical in FPP/xLights: WS281x timing, same global controller options.
  • Tried "slow" timing mode for WS281x on all ports.
  • Result: no improvement on Port 2/3.
  • Addressing and ranges
  • Ranges/universes created and uploaded from xLights; verified continuous, no overlaps.
  • In FPP Display Testing, enabled each port's range in isolation.
  • Result: Port 2 still flickers even when driven alone.
  • SRx internal test pattern
  • Stopped FPP output.
  • Enabled SRx internal test pattern.
  • Result: all four SRx ports run clean with the internal pattern.
  • Logical port swap (software remap)
  • In FPP, swapped the channel ranges for Port 1 and Port 2 (1 ↔ 2), keeping all physical wiring unchanged.
  • Also tested each swapped range in Display Testing separately.
  • Result: flicker remains on the same physical connector (Port 2), even when driven with Port 1's logical range.
  • Power and reboots
  • Full power cycle of KULP32 and SRx (10–15 s off).
  • Result: no change.
  • Connector check
  • Swapped Phoenix plug assemblies between ports to rule out connector issues.
  • Result: fault does not follow the plug; remains on SRx Port 2 (and earlier, Port 3).
Current assessment
  • Since the SRx's internal test pattern is clean for all ports, but any data from the KULP 32AB/FPP path causes flicker only on the same physical SRx port, this points to a problem on the differential data path for Port 2 (and possibly Port 3) between the KULP 32AB and SRx. The issue does not appear to be pixel type, timing, addressing, or cabling to the pixels.
What I'm looking for
  • Has anyone seen a SRx v4.01/KULP 32AB case where the internal pattern is fine but external data flickers on a specific receiver port?
  • Any known firmware quirks for SRx v4.01 or KULP 32AB that affect ports 2/3 specifically?
  • Recommended additional diagnostics to pinpoint whether the fault is on the KULP 32AB transmitter channel vs. the SRx receiver channel for Port 2 (e.g., suggested cross‑patch tests on the differential outputs)?
  • Before I RMA: any other settings to check for Smart Receiver v2 chains with a single receiver (Receiver A) that could cause this symptom?
Temporary workaround
  • I can run on SRx Ports 1 and 4 for now, but I'd like to restore Ports 2/3 if possible.
Thanks in advance for any pointers or confirmation that this is likely a hardware channel failure on the differential link.
Pixel noob
davidr236
Did you ever find a solution? Mine is doing the same thing, except from a falcon f16v3.
ricardo
Yes, my friend, I did find the reason. The problem was actually with my network cable. It had a cable where two of the eight wires were not connected properly. So, I used one of those RJ45 cable testers and it showed that there were two with errors. Then I replaced the cable and everything worked fine.